Issue
A BACnet Binary Input object cannot be added to a Niagara R2 container.
Environment
Workplace Pro
Cause
In Workplace Pro, BACnet objects must be placed under BACnet devices.
Resolution
- Copy a BACnet Device from the Local Library (/tridiumx/BACnet/objects/BACnetDevice) into the container
- Add the BACnet object under the device.
- For more information, refer to the BACnet Integration Reference.