Issue
System Plug-In returns "Error: 80010105" when downloading a programmable controller.
Environment
Vista Server
NL220 / Lonmaker
System Plug-In
Cause
The cause is unknown at this time. When downloading a controller through System Plug-in this error will stop the download from proceeding. It seems to be system-wide once it happens, not controller related.
Resolution
- Go to Start > Settings > Control Panel > Add or Remove Programs
- Uninstall the TAC Toolpack
- Re-Install TAC Toolpack (make sure it matches the Vista Server version).