41353members
184432posts

7798C cannot be used with I/NET 2000

7798C cannot be used with I/NET 2000

Issue

Can a 7798C be used in an I/NET 2000 System?

Product Line

TAC INET

Environment

  • I/NET 2000
  • I/NET Seven rev 1.16 and above
  • 7798C SLI

Cause

AMT is different in I/NET 2000 than it is in I/NET Seven and any message and transaction from this SLI will not report correctly.

Resolution

  • This SLI cannot be used in I/NET 2000. 
  • Even if 7798C Bin files are loaded into I/NET 2000, the SLI will not work.
  • This SLI is designed to ONLY operate correctly in I/NET Seven Rev 1.16 and above.
Tags (3)
Labels (1)
No ratings