Posted: 2023-03-2709:10 PM
Video - How to communicate between two M580 PLC using OPCUA client on M580 firmware 4.xx
We have try to download the attachment file of the video, but we are not able to open the UAClient STA? May I know who is the contact person of this FAQ000247881? As I want to further investigate more detail on this communication.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-2810:03 AM
What version of Control Expert are you using to Open the .sta, I tried with 15.2 and got this error: "M580 Master: The version of the DTM stored in the Database (2.16.31.0) is higher than the cersin of the DTM installed on the PC (2.16.29.0)"
You'll have to find the updated DTM (I can't find it) or switch to Control Expert 15.3 which includes the 2.17.24 DTM (I don't know if it is backwards compatible, but generally they are).