how can i make configurations and change parameters on my SE8000 from pc ?

Highlighted

how can i make configurations and change parameters on my SE8000 from pc ?

which software do i need ?

do i need smartx controller or just MPM?

how can i make configurations?

Tags (1)
1 REPLY 1
Highlighted
Administrator

Re: how can i make configurations and change parameters on my SE8000 from pc ?

The SE8000 Room Controllers do not have any configuration software or GUI. All configuration and settings can be accomplished from the local display. The controllers are designed to communicate with a supervisory system via Zigbee, BACnet, Modbus or WiFi. What supervisory system you use depends on the communication options purchased with the controller.

 

This could be any BACnet controller such as a SmartX Server, a modbus master such as a SmartX Server or HRC, an MPM if Zigbee is used.

 

Maybe if you tell us what outcome you are looking for we can assist further, however I'd recommend discussing this with an experienced system integrator in you region.