TAC Xenta OP just shows "Connecting to Xenta base unit"

Hello,

 

I have a TAC Xenta OP and a TAC Xenta 301 (controlling the heating system).

When connecting the two (with the DP-Jack), the OP just shows "Connecting to Xenta base unit". Additionally I recognize, that the font is quite faded.

A technician with another OP could connect to the Xenta 301 just fine, but I remember his OP having a blue instead of the red frame. So I don't know if it also was an TAC Xenta OP.

 

Are there incompatible Versions of TAC Xenta OP and TAC Xenta 301?

How could I check the OP?

 

I would appreciate any hint.

 

P.S.: As I just want to check the parameters of the heating system from time to time: is there another way, like through the RS232 interface (I guess that is only for programming the Xenta) or with an software-emulated OP?

 

Best regards,

Christoph

Tags (4)
1 REPLY 1
Highlighted

Re: TAC Xenta OP just shows "Connecting to Xenta base unit"

Have it been working before?

This could be due to wrong address settings.

Do you know what domain and subnet/node your TAC Xenta 301 are using?

The TAC Xenta OP must be on the same domain.