I've got 2 separate systems running an mpm and recently had a power failure that seemed to lock both into bootloader. I got one to boot by cycling power but haven't had any luck with the other. Suggestions?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-28 06:20 PM
Try restoring factory settings through the bootloader. Hopefully you have a backup of the database!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-28 06:20 PM
Try restoring factory settings through the bootloader. Hopefully you have a backup of the database!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-28 06:23 PM
I have the original database that was loaded. I never pulled it from the mpm once I got the system balanced. I'm guessing I'll have to do that again? Rebind the room controllers and all?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.