Enter the EcoStruxure Power Monitoring community of experts and find answers to your questions about the EcoStruxure Power Monitoring Expert software. From IoT implementation to sensor integration and more, get support from experts and share your experiences by subscribing to the Schneider Electric Exchange forum today.
Link copied. Please paste this link to share this article on your social media post.
Hi all,
I didn't configured Power Tag before. May i get the documents and links regarding How to add and configure Power Tag in PME?
Thanks,
Link copied. Please paste this link to share this article on your social media post.
You have to use smartlink In order to use PowerTag. It has web page where you can discover and configure the PowerTag connected to it. After that smartlink will act as a gateway to Modbus for PowerTags. So you can simply add the modbus TCP gateway in PME and create the PowerTag as Modbus RTU devices.
Link copied. Please paste this link to share this article on your social media post.
Hello @jagadeesh_s , I add @Calvin_HopWo to this thread, he should be able to help you!
PS: do not hesitate to check the Knowledge base & use the global search bar to see if your issue was already raised before 😉
Link copied. Please paste this link to share this article on your social media post.
You have to use smartlink In order to use PowerTag. It has web page where you can discover and configure the PowerTag connected to it. After that smartlink will act as a gateway to Modbus for PowerTags. So you can simply add the modbus TCP gateway in PME and create the PowerTag as Modbus RTU devices.
Link copied. Please paste this link to share this article on your social media post.
Sorry to bother you but do you know how to configure powertag attached to Acti9link attached to a Com'X?
Link copied. Please paste this link to share this article on your social media post.
Do you mean PowerTag attached to Smartlink? If I'm right then You don't need the Com'X, because Smartlink Ethernet is already has the Modbus RTU to Modbus TCP gateway feature. You have to open the smartlink web page and scan the powertag. When the searching will finish You will see all powertag on searching page. Each PowerTag will have the modbus address. And since this time this Smartlink Ethernet will act as Modbus gateway for the PowerTags. You dont need the Com'X. Also Smartlink Ethernet supports 10 RS485 devices connected to RS485 port and act as Modbus TCP gateway for it. You can connect Smartlink RS485, Power meters or another Modbus RTU devices.
Smartlink RS485 does not support the PowerTags.
Link copied. Please paste this link to share this article on your social media post.
Yeah, thank you man.
I figured it out after some tries.
I couldn't use the smartlink itself 'cause it was attached under the 2nd ETH port of the Com'X with a different IP class... and I found out that I should've used the "local ID" instead of the "Slave ID" to integrate them on PME.
Thank you again for your fast answer.
Have a nice day.