Citect Import Tags

How do you import tags from unity pro(Ecostruxure) to citect? The only thing I have found is to address all tags manually, which seems excessive for two products under Schneider. 

1 REPLY 1
Highlighted
Commander

Re: Citect Import Tags

Hi @jm , you can use OFS for automatic import tag from Unity PLC. 
before tha you need to open Project Setting, to checked option Data Dictionary in Unity Pro / Control Expert, you can also checked "HMI variable only" if you want to filter it.

 
 

image.png