Drive fault output side is OK. But fault is active.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-30 08:41 AM
Is it a commissioning or was it running before ? In case of commissioning, ensure you have entered motor name plate and did an autotuning.
In case of a sudden failure detection, check the system with another motor (could be smaller).
When you say 0V at output, in this case what are the status/settings of I/O (digital inputs) as well as the analogue input (position of potentiometer or speed reference .
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2020-07-21 09:29 PM
Motor and cables of invertor is OK. I have disabled the fault from drive. But after that I checked output voltage in invertor it is showing is '0' I need to know is this invertor internal fault or not. If internal fault how to solve this.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-03-30 08:41 AM
Is it a commissioning or was it running before ? In case of commissioning, ensure you have entered motor name plate and did an autotuning.
In case of a sudden failure detection, check the system with another motor (could be smaller).
When you say 0V at output, in this case what are the status/settings of I/O (digital inputs) as well as the analogue input (position of potentiometer or speed reference .