A support forum for AVEVA Plant SCADA (formerly Citect SCADA). Share new and exciting product information, connect, learn, and collaborate with the ecosystem of Plant SCADA Users. AVEVA Plant SCADA a reliable, flexible and high-performance Supervisory Control and Data Acquisition software solution for industrial process customers. This forum is to connect, share, learn and collaborate new and exciting product information. Feel free to join and share to your Ecosystem of Plant SCADA Users.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-06-07 04:45 AM
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-11-03 05:11 AM
Hi @thais.claudino ,
Most likely, this issue may be due to the fact that you have created an user with the name "user" in your project; try to modify its name and everything should work as expected.
Best regards,
Andrea
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2023-12-02 01:07 AM
You try check box at "Accept encrypted and non-encrypted connections (mixed mode). I encountered a problem when configuring OPCUAServer.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2024-01-18 10:38 PM
hei, @ElFago ,
i have same problem. tried find user name but we don't have. do you know what i can do to fix this problem?