Hi!
I have a back -ups 700, a few days started to whistle continuously and sockets are not powered.
I purchased a new battery to replace the original, but the problem is not solved.
What may have happened ?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:13 AM . Last Modified: yesterday
Hi,
The UPS should not make a whistling noise. You can try a reset to see if the issue clears
1: Disconnect any attached load.
2: Unplug the UPS from the wall socket.
3: Disconnect the UPS' internal battery.
4: Push and hold the "On" button on the UPS for 5 seconds
5: Reconnect internal battery.
6: Plug UPS in to known good power source.
7: Turn UPS on.
If the unit continues to whistle after the reset it should be replaced.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:13 AM . Last Modified: yesterday
Hi,
The UPS should not make a whistling noise. You can try a reset to see if the issue clears
1: Disconnect any attached load.
2: Unplug the UPS from the wall socket.
3: Disconnect the UPS' internal battery.
4: Push and hold the "On" button on the UPS for 5 seconds
5: Reconnect internal battery.
6: Plug UPS in to known good power source.
7: Turn UPS on.
If the unit continues to whistle after the reset it should be replaced.