Posted: 2021-06-29 08:28 AM
This was originally posted on APC forums on 7/14/2012
I am not sure where the battery percentage was when I plugged it in this morning because I had not installed the software yet but I do know the display was showing three bars. Went out for about 5 hours and I come back and there are only two bars showing and the percentage was at 48%. After another two hours it was at 44%. I ran the self test and it jumped back to 58% then within 40 minutes or so it was back down to 48% and seems to be hovering there. Anybody know what the deal is with this issue? I purchased it yesterday evening.
BTW - What is the model number? The unit and box are XS1000 the sticker with the serial and model number show BX1000G, and when I open the technical window in the software it displays RS1000G.... Confused!
Thank you,
Bill S
Posted: 2021-06-29 08:28 AM
This was originally posted on APC forums on 7/16/2012
I have two of these & one 1500.
The 1000's have a brain fart from time to time. You need to:
turn it off
unplug the power cord
remove the battery
push the power on button for a few seconds
let it sit for a couple of minutes
install the battery
plug it back in to ac power
Posted: 2021-06-29 08:28 AM
This was originally posted on APC forums on 7/15/2012
The battery level on the screen and in the software now says 0%...
Posted: 2021-06-29 08:28 AM
This was originally posted on APC forums on 7/16/2012
I have two of these & one 1500.
The 1000's have a brain fart from time to time. You need to:
turn it off
unplug the power cord
remove the battery
push the power on button for a few seconds
let it sit for a couple of minutes
install the battery
plug it back in to ac power