Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
Using low loads with UPSs...
APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-0106:10 PM
Using low loads with UPSs...
I have a need to keep power to devices that are in stand-by mode in the event of a power outage. Those devices draw about 2.5 watts and 70mA according to their respective specs.
I had hoped to use APC units like the BE 550 and ES 725 because I already own them. I'm finding inconsistent information regarding minimum load. Some people report that back-ups won't work with such low loads and others claim they've used them successfully.
One way is to test, which I'm willing to do - but first I thought I'd ask here to see if I could get some opinions or actual facts.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-1704:15 AM
Hi,
Some Back UPS have a feature called "Low Load Shutdown". This feature shuts down the UPS after 15 minutes if the load is below 15 - 20W. If the UPS you wish to buy has this feature, then it will not be able to provide a back up for a load of 2.5W.