Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79501members
344298posts

Using a APC NS 1250 (Model BN1250) on other electronics

Solved
LikinAPC123_apc
Cadet
0 Likes
2
137

Using a APC NS 1250 (Model BN1250) on other electronics

This was originally posted on APC forums on 3/27/2011


Can I use this Back-Ups unit for a widescreen tv and DVR, etc? I bought a used one that seems to be working fine and have used a smaller unit for a computer and monitor but hesitate to use it for my TV, etc.


Accepted Solutions
ginbot86_apc
Lieutenant JG
Lieutenant JG
0 Likes
0
137

Re: Using a APC NS 1250 (Model BN1250) on other electronics

This was originally posted on APC forums on 5/3/2011


A sine wave moves smoothly up and down, but the cheaper UPS models output a 'modified sine wave' which basically has zero volts, a step of positive voltage, zero volts, a step of negative voltage, and so on. This is done to minimize 'harmonic frequencies' which would otherwise cause energy to be wasted as heat, while keeping the total cost (and weight) of the UPS low.

See Answer In Context

2 Replies 2
LikinAPC123_apc
Cadet
0 Likes
0
137

Re: Using a APC NS 1250 (Model BN1250) on other electronics

This was originally posted on APC forums on 3/29/2011


Thanks for your response to my question - Now I'll go and find out what "step approximation to a sine wave" means but I feel better about trying it.

ginbot86_apc
Lieutenant JG
Lieutenant JG
0 Likes
0
138

Re: Using a APC NS 1250 (Model BN1250) on other electronics

This was originally posted on APC forums on 5/3/2011


A sine wave moves smoothly up and down, but the cheaper UPS models output a 'modified sine wave' which basically has zero volts, a step of positive voltage, zero volts, a step of negative voltage, and so on. This is done to minimize 'harmonic frequencies' which would otherwise cause energy to be wasted as heat, while keeping the total cost (and weight) of the UPS low.