Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79503members
344311posts

UPS XS 1300 LCD

Solved
jimc_apc
Crewman
Crewman
0 Likes
4
110

UPS XS 1300 LCD

This was originally posted on APC forums on 5/17/2009


Brand new, bought at costco. Has worked for past 2mo, but 1wk ago unit shut down while I was out of town for the week. Going by the recording schedule from my satellite receiver, unit shut down the night I left. I powered it back on thinking there was an outage while I was away and it drained the battery, seemed to work fine. Woke up this morning and it was off again. Powered it up and looked at display, both load and battery indicator are empty. Battery replacement indicator is not displayed.


Accepted Solutions
jimc_apc
Crewman
Crewman
0 Likes
0
110

Re: UPS XS 1300 LCD

This was originally posted on APC forums on 5/18/2009


Went straight to the connections and that was apparently the problem. Thx for the diagnosis and treatment.

See Answer In Context

4 Replies 4
BillP
Administrator Administrator
Administrator
0 Likes
0
110

Re: UPS XS 1300 LCD

This reply was originally posted by Angela on APC forums on 5/17/2009


is the UPS still providing output power even though it turned off by itself? do you still have items plugged into it? is the battery indicator empty and solid or is it flashing empty? when you turned the unit back on the first time it went off, does the UPS do a self test (go to battery for ~20 seconds)?

jimc_apc
Crewman
Crewman
0 Likes
0
110

Re: UPS XS 1300 LCD

This was originally posted on APC forums on 5/18/2009


is the UPS still providing output power even though it turned off by itself? yes
do you still have items plugged into it? yes
is the battery indicator empty and solid or is it flashing empty? latter
when you turned the unit back on the first time it went off, does the UPS do a self test (go to battery for ~20 seconds)? i didnt look at it the first time, when i do the self test it shows as online, there is voltage coming in and batt ind is flashing empty

BillP
Administrator Administrator
Administrator
0 Likes
0
110

Re: UPS XS 1300 LCD

This reply was originally posted by Angela on APC forums on 5/18/2009


okay so while the battery indicator is flashing, if you plug a non critical piece of equipment does the UPS turn off?

a flashing empty battery icon indicates the battery is disconnected. if the UPS turns off on the above test, then i would double check the battery connections and reseat them. you could reseat them first before trying that test.

jimc_apc
Crewman
Crewman
0 Likes
0
111

Re: UPS XS 1300 LCD

This was originally posted on APC forums on 5/18/2009


Went straight to the connections and that was apparently the problem. Thx for the diagnosis and treatment.