Posted: 2021-06-29 08:12 PM
This was originally posted on APC forums on 11/5/2009
I'm trying to figure out what size generator we need to get to work with a new Symmetra 16kW UPS we're installing. I'm being told 1.5 times, 3 times and 5 times the size, which equates to 25kw, 45kw and 70kw. This all seems so fuzzy and no one I talk to will commit to guarantee me that their recommendation will work except the guy telling me to get a 70kw unit. What I'm hearing is that the UPS doesn't see that the generator is providing power and so it switches back and forth between battery mode and utility line mode until the battery finally shuts down.
Anyone have any experience or history with this that actually knows exactly what to do?
Don't get me wrong, I appreciate feedback, but I don't need any more "Well I heard..." or "from what I've been told..." I need an "I have X size generator installed with an X size UPS and it works perfectly."
Thanks for any light that can be shed.
Posted: 2021-06-29 08:12 PM
This was originally posted on APC forums on 11/22/2009
Posted: 2021-06-29 08:12 PM
This was originally posted on APC forums on 11/5/2009
I would recommend reading these white papers to determine the proper thinking that goes along with adding a generator to your IT facility.
http://www.apcmedia.com/salestools/SADE-5TNRKS_R0_EN.pdf
http://www.apcmedia.com/salestools/SADE-5TNNEP_R4_EN.pdf
http://www.cumminspower.com/www/literature/technicalpapers/PT-7007-SizingGensets-en.pdf
Posted: 2021-06-29 08:12 PM
This reply was originally posted by Matt on APC forums on 11/12/2009
Hi Rushweb,
A quick search for "Symmetra generator" in the kBase at www.apc.com/support returns the article "[Generator Sizing for Single-Phase Symmetra UPS Systems|http://nam-en.apc.com/cgi-bin/nam_en.cfg/php/enduser/std_adp.php?p_faqid=7300]."
Here is the full text of the article:
"A generator, Genset, should be sized to 1.5 times the size of the Symmetra's full capacity.
Many standard off-the-shelf Gensets are sized at 0.8 power factor for continuous duty operation ( > 30 mins of runtime ). When the Genset is sized < 1.5 times Symmetra frame size, the interaction of the Symmetra PFC (power factor corrected) circuitry with output impendence of the generator results in generator output waveform distortion. This distortion can lead to alarms on the Symmetra related to input voltage & frequency.
For these reasons, the recommendation is to size the generator at 1.5 times the Symmetra's full capacity and not exceed 75% of the generator's load capacity. (This load includes other devices that may be powered by the generator but not by the UPS such as AC, heating, and lighting)."