I have several Smart-UPS 1500 UPS units in service and two spare units were inadvertently stored for more than a year without being plugged in. When they were discovered, I bought and installed replacement batteries for them. When I powered them up, they come up dead with no LEDs and the power switch(s) inoperative.
Do these units just die without remedy if they are un-powered for a long period?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:19 AM . Last Modified: 2024-03-22 12:53 AM
25.2 Vdc, Measured
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:19 AM . Last Modified: 2024-03-22 12:53 AM
I tried the cold start routine and one of them returned to normal (I didn't know about the cold start routine). The other one comes up in the UPS back-up mode and does not recognize the line--must be a real failure. THANK YOU for answering my question. I now have one good one!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:19 AM . Last Modified: 2024-03-22 12:53 AM
25.2 Vdc, Measured
Link copied. Please paste this link to share this article on your social media post.