Schematics for SC1500

This was originally posted on APC forums on 10/8/2011


I was replacing the batteries to a Smart-UPS SC 1500 and I got the leads mixed up. Does anyone have a schematic for this power supply? I just need the wiring document for the 4 batteries.


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
160

Re: Schematics for SC1500

This reply was originally posted by Dakota on APC forums on 10/8/2011


Apc Wont Offer Them But I Can Probably Get Them What Is The EXTACT Model Number Of The Ups

See Answer In Context

5 Replies 5
DaveS_apc
Crewman
Crewman
0 Likes
0
160

Re: Schematics for SC1500

This was originally posted on APC forums on 10/10/2011


Smart-UPs SC 1500

jms_apc
Crewman
Crewman
0 Likes
0
160

Re: Schematics for SC1500

This was originally posted on APC forums on 1/14/2014


I also have a Smart UPS 1000. Model SUA1000   AS0520323347

Any chance you could find a schematic for this?

Battman_apc
Commander
Commander
0 Likes
0
160

Re: Schematics for SC1500

This was originally posted on APC forums on 1/14/2014


The four batteries in this ups (which I think has an RBC59 cartridge) are connected as two series strings which are  in parallel  with each other.... IE

( + ) -----  [+  Bat 1   -]---[+ Bat 2   -]----   ( - )

        \                                                 /

         \---  [+  Bat 3  - ]---[+ Bat 4  -]--/

Hope my ASCII art doesn't get mangled in translation !

BillP
Administrator Administrator
Administrator
0 Likes
0
159

Re: Schematics for SC1500

This reply was originally posted by Dakota on APC forums on 10/13/2011


That Is Not The Exact model number what is the serial number

BillP
Administrator Administrator
Administrator
0 Likes
0
161

Re: Schematics for SC1500

This reply was originally posted by Dakota on APC forums on 10/8/2011


Apc Wont Offer Them But I Can Probably Get Them What Is The EXTACT Model Number Of The Ups