Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
80570members
346453posts

SUV650

Solved
airboy64_apc
Crewman
Crewman
0 Likes
2
97

SUV650

This was originally posted on APC forums on 11/28/2011


I have a Smart-UPS with a sticker on it that says the model is a SUV650. My question is this... on-battery power I am seeing about 85volts with a standard Fluke 77 multimeter. Is this normal relative to the output waveform this particular unit produces?

Tags (1)

Accepted Solutions
airboy64_apc
Crewman
Crewman
0 Likes
0
97

Re: SUV650

This was originally posted on APC forums on 11/28/2011


Thanks, I had sort of read this before which is why I mentioned my multimeter, although I had thought simply thought that BACK-UPS used the stepped waveform and SMART-UPS did not. Now I see that some of the SMART-UPS do as well.
Thanks very much.

See Answer In Context

2 Replies 2
BillP
Administrator Administrator
Administrator
0 Likes
0
97

Re: SUV650

This reply was originally posted by Chris on APC forums on 11/28/2011


This is normal. Please read the document at the link below for an explanation

http://nam-en.apc.com/app/answers/detail/a_id/1493/kw/step approx

airboy64_apc
Crewman
Crewman
0 Likes
0
98

Re: SUV650

This was originally posted on APC forums on 11/28/2011


Thanks, I had sort of read this before which is why I mentioned my multimeter, although I had thought simply thought that BACK-UPS used the stepped waveform and SMART-UPS did not. Now I see that some of the SMART-UPS do as well.
Thanks very much.