SUV650

This was originally posted on APC forums on 11/28/2011


I have a Smart-UPS with a sticker on it that says the model is a SUV650. My question is this... on-battery power I am seeing about 85volts with a standard Fluke 77 multimeter. Is this normal relative to the output waveform this particular unit produces?

Tags (1)

Accepted Solutions
airboy64_apc
Crewman
Crewman
0 Likes
0
99

Re: SUV650

This was originally posted on APC forums on 11/28/2011


Thanks, I had sort of read this before which is why I mentioned my multimeter, although I had thought simply thought that BACK-UPS used the stepped waveform and SMART-UPS did not. Now I see that some of the SMART-UPS do as well.
Thanks very much.

See Answer In Context

2 Replies 2
BillP
Administrator Administrator
Administrator
0 Likes
0
99

Re: SUV650

This reply was originally posted by Chris on APC forums on 11/28/2011


This is normal. Please read the document at the link below for an explanation

http://nam-en.apc.com/app/answers/detail/a_id/1493/kw/step approx

airboy64_apc
Crewman
Crewman
0 Likes
0
100

Re: SUV650

This was originally posted on APC forums on 11/28/2011


Thanks, I had sort of read this before which is why I mentioned my multimeter, although I had thought simply thought that BACK-UPS used the stepped waveform and SMART-UPS did not. Now I see that some of the SMART-UPS do as well.
Thanks very much.