Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79501members
344296posts

SUA3000XLI + (1)SUA48XLBP 24 hrs 58 mins @ 50W

Solved
lsco_apc
Crewman
Crewman
0 Likes
2
76

SUA3000XLI + (1)SUA48XLBP 24 hrs 58 mins @ 50W

This was originally posted on APC forums on 5/18/2010


For the captioned models of UPS + Battery Pack, I have tested the UPS could maintain less than 18 hrs instead of 24hrs.

The following shows the on-site measurement of power consumption.

0.26A x 220V = 57.2W at full load
0.09A x 220V = 19.8W at part load

Note that, the system is running at part load condition for UPS testing.

Could someone tell me what is happening?

Many Thanks!


Accepted Solutions
lsco_apc
Crewman
Crewman
0 Likes
0
76

SUA3000XLI + (1)SUA48XLBP 24 hrs 58 mins @ 50W

This was originally posted on APC forums on 5/18/2010


For the captioned models of UPS + Battery Pack, I have tested the UPS could maintain less than 18 hrs instead of 24hrs.

The following shows the on-site measurement of power consumption.

0.26A x 220V = 57.2W at full load
0.09A x 220V = 19.8W at part load

Note that, the system is running at part load condition for UPS testing.

Could someone tell me what is happening?

Many Thanks!

See Answer In Context

2 Replies 2
lsco_apc
Crewman
Crewman
0 Likes
0
75

Re: SUA3000XLI + (1)SUA48XLBP 24 hrs 58 mins @ 50W

This was originally posted on APC forums on 5/26/2010


http://www.apc.com/resource/include/ups_runtime_chart.cfm?base_sku=SUA3000XLI&family_id=165

The above link is shown how I was selected for this model.

lsco_apc
Crewman
Crewman
0 Likes
0
77

SUA3000XLI + (1)SUA48XLBP 24 hrs 58 mins @ 50W

This was originally posted on APC forums on 5/18/2010


For the captioned models of UPS + Battery Pack, I have tested the UPS could maintain less than 18 hrs instead of 24hrs.

The following shows the on-site measurement of power consumption.

0.26A x 220V = 57.2W at full load
0.09A x 220V = 19.8W at part load

Note that, the system is running at part load condition for UPS testing.

Could someone tell me what is happening?

Many Thanks!