I have SMC1000IC. I can connect to UPS through Serial port or USB port with PowerChute Business Edition and I can get battery status from web interface.
In my application I can't use PowerChute. I need to get information if UPS is powered from Battery or AC and information if battery is empty. Is this possible?
Posted: 1 week ago
Enable advanced menu, then see if there is a Modbus function you can enable, if it's possible then you can communicate using Modbus RTU over the serial.
Posted: Tuesday
SMC model UPS do not support Modbus. The SMT model Smart-UPS do.
See Schneider Electric "Modbus Implementation in APC Smart-UPS."