Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79103members
343440posts

Questions with BX1300LCD (PICS)

mckayman_apc
Crewman
Crewman
0 Likes
0
84

Questions with BX1300LCD (PICS)

This was originally posted on APC forums on 5/8/2013


Hello everyone, I have a few questions regarding the BX1300LCD unit. I was just was given a broken BX1300LCD. The problems were, the fuses were blown and the large 22uf 400v cap was popped. A really easy fix to do on such a nice unit. I have been repairing electronics for many years so I am quite comfortable and knowledgeable when working on circuit boards. I replaced the fuses and capacitor, now the BX1300LCD functions perfect! Good as New! =D Oscilloscope verified the wave form output is correct on battery. Floating potential charge for the batteries is correct as well. I have downloaded the manual and have read it thoroughly. The question I have is, what exactly are these jumpers for on the main board up near the display?

Thanks!


Attachments