Posted: 2021-06-29 07:13 PM
This was originally posted on APC forums on 11/27/2008
I m try to conect to managment card and when i'm install Network Shutdown client on other computer. I see next message "Security information did not match information at 192.168.1.91". I can go on http protocol on managment card. What is it problem?
Posted: 2021-06-29 07:14 PM
This reply was originally posted by Angela on APC forums on 1/31/2012
ok, so it is what i expected. the only two issues that can cause this are you did not use the same administrator username for PCNS as what is used as the administrator username and password on your network management card (which appeared to be apc per your screenshot) or that authentication phrase in my screenshot is wrong.
did you use apc as the username when you installed PCNS? did you reset the authentication phrase on the NMC back to admin user phrase (case sensitive)? then you need to type it the same way when PCNS prompts for it.
if you did, i might reset the network management card to defaults, excluding TCP/IP. you could back up the config.ini file from it first which can be done via FTP. instructions on doing that are here if this device is on the public side of struxureware central or if it is on the private side, you'd need to connect to that private side and back it up via FTP. i am thinking a reset might be good if something is corrupt.
Posted: 2021-06-29 07:13 PM
This was originally posted on APC forums on 11/1/2011
Hi
Sorted thank you. For some reason the authentication phrase was different on the powerchute to the NMC, even though it was a default install..?
Set them both back to defaults all fixed.
Thanks again
Message was edited by: grum13
Posted: 2021-06-29 07:14 PM
This reply was originally posted by Annie on APC forums on 11/27/2008
Hi
What's NMC card firmware version? What user/password/authentication phrase did you type during PCNS install? Please note the administrator user name and authentication phrase authenticate the communication between PCNS and the NMC. Because of this you must set the values in PCNS to match the values for the NMC. (Note that it is allowable to set a password for PCNS that is different from the password for the NMC.)
In the NMC, the default administrator user name and password are both apc. The default setting for the authentication phrase is admin user phrase. If you input the correct user/password/auth phrase, the issue still occured, you may need to login to the card via web browser and navigate to UPS-PowerChute-Configuration(under PowerChute) to change auth phrase. After that, login off. Then install the PCNS again and type the user/auth phrase that same as those in the card. Hope it helps.
Posted: 2021-06-29 07:14 PM
This was originally posted on APC forums on 1/27/2012
Hi
I am currently having the same issue described in the original thread however, when I reset the credentials to be the same across the board, I'm still getting the mis-matched error. We have changed the password for log ins to the NMC but I triple checked to make sure I'm typing everything in correctly and everything should match up.
Any other tips?
Thank you.
Message was edited by: dgriffith@i3.com
Message was edited by: dgriffith@i3.com
Posted: 2021-06-29 07:14 PM
This was originally posted on APC forums on 1/30/2012
Oh, sorry, yes I had. And I had installed and ran PC on another machine with the same settings/credentials.
Posted: 2021-06-29 07:14 PM
This reply was originally posted by Angela on APC forums on 1/30/2012
how and where are you resetting the credentials? can you be more specific so we can ensure you got everything?
Posted: 2021-06-29 07:14 PM
This was originally posted on APC forums on 1/30/2012
Sure
I attached a screen shot. I'm logged into InfraStruxure Central, then logged into the UPS.
Message was edited by: dgriffith@i3.com
Message was edited by: dgriffith@i3.com
Posted: 2021-06-29 07:14 PM
This reply was originally posted by Angela on APC forums on 1/30/2012
have you changed the powerchute authentication phrase? the screenshot you showed me is the username and password for the NMC itself.
Check under the NMC UPS tab and then look for powerchute configuration. you need to make sure the authentication phrase listed in that section is the same as it is when you install powerchute network shutdown. the default that you can set it to is admin user phrase
see my screenshot i attached.
Posted: 2021-06-29 07:14 PM
This reply was originally posted by Angela on APC forums on 1/30/2012
can you post a screenshot of the result you get? just want to ask around and have something to show and clarify. thanks.
the normal things that cause security mismatch are incorrect username between PCNS and NMC (username must match) and then the authentication phrase being incorrect that i showed.
Posted: 2021-06-29 07:14 PM
This reply was originally posted by Angela on APC forums on 1/31/2012
ok, so it is what i expected. the only two issues that can cause this are you did not use the same administrator username for PCNS as what is used as the administrator username and password on your network management card (which appeared to be apc per your screenshot) or that authentication phrase in my screenshot is wrong.
did you use apc as the username when you installed PCNS? did you reset the authentication phrase on the NMC back to admin user phrase (case sensitive)? then you need to type it the same way when PCNS prompts for it.
if you did, i might reset the network management card to defaults, excluding TCP/IP. you could back up the config.ini file from it first which can be done via FTP. instructions on doing that are here if this device is on the public side of struxureware central or if it is on the private side, you'd need to connect to that private side and back it up via FTP. i am thinking a reset might be good if something is corrupt.