Posted: 2021-06-28 08:39 AM
This was originally posted on APC forums on 4/30/2020
Hi,
I have a UPS SUA3000. If the UPS enters in battery mode until is exhausted and then the power back on, is the power restored to all devices conected to the UPS automatically? or do I have to power on manually the UPS in order to restored. I do not see any option in the powerchute software to control this
rgds
Andy
Posted: 2021-06-28 08:39 AM
This reply was originally posted by Bill on APC forums on 5/4/2020
Hi,
The default setting is to restore power to the outlet group when AC returns. If you are running PowerChute 9.5 or 10 you will find the setting under Shutdown - Outlet Sequence
Posted: 2021-06-28 08:39 AM
This reply was originally posted by Bill on APC forums on 5/4/2020
Hi,
The default setting is to restore power to the outlet group when AC returns. If you are running PowerChute 9.5 or 10 you will find the setting under Shutdown - Outlet Sequence