We have 2 PDU's that are 24A 200-240v. My question is, does this need to be plugged into a "2 pole" circuit?
I have a receptacle with is L6-30, and the breakers are 1 pole 120/240. Would this work with the PDU's? Or do I have to have a 2 pole circuit with these PDU's?
Thanks to anyone who can help.
Message was edited by: ekrengel
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:12 PM . Last Modified: 1 week ago
It depends on where in the world you are. In the US, then yes, because 208/230v are provided phase to phase.
In Europe, no, because, 230v comes from phase-to-neutral from a 400Y230V system.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:12 PM . Last Modified: 1 week ago
It's not an APC pdu, it was just a general power question. I got it answered from an electrician though. A 24amp 200/240v PDU does need to have an 2 pole 30A breaker.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:12 PM . Last Modified: 1 week ago
Eric,
For us to better assist you, would it be possible for you to provide us with the model number of your PDU?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 08:12 PM . Last Modified: 1 week ago
It depends on where in the world you are. In the US, then yes, because 208/230v are provided phase to phase.
In Europe, no, because, 230v comes from phase-to-neutral from a 400Y230V system.