Hi,
I have a AR3104 Rack, and by reading the installation documentation for the AP9567 PDU, it states that PDU can only be toolessly installed on a NetShelter VX rack.
But on the main page for the AP9567 PDU, it makes no mention of being specific to the VX series racks.
Can someone confirm if the AP9567 PDU will be compatible with the AR3104 NetShelter SX rack. By that I mean just click the PDU on the side rear support plate of the rack so it doesn't take up any U's ?
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:47 PM . Last Modified: 1 week ago
Perfect..
Thanks for the confirmation.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:47 PM . Last Modified: 1 week ago
unfortunately, i dont think this model's documentation has been updated recently. this product will work fine with Netshelter SX as the VX line is discontinued. The PDU will mount in the 0U channel as you described with the toolless mounting pegs on the back of the PDU.
hope that helps
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 09:47 PM . Last Modified: 1 week ago
Perfect..
Thanks for the confirmation.