Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
My computer won't turn on in battery mode (UPS brand new)
APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-01-1906:20 AM. Last Modified: 2022-01-1906:30 AM
My computer won't turn on in battery mode (UPS brand new)
Hi. My computer won't turn on in battery mode with the APC BX-1500M-LM60 1500va (900w)
The consumption of my computer is approximately only 500 watts. The same UPS show this in the display but is not working in battery mode. When the electrical service fails then my UPS can't turn on my computer, because it only turns on some RGB lights. No video signal, the rest of the pc stays off. 😞
My UPS is totally brand new
My PC have i9 900K processor, 9 rgb fans, 1 hdd, 1 M.2 NVME, RTX 3070 and ENERMAX 1200w Platinum power supply
Link copied. Please paste this link to share this article on your social media post.
Posted: 2022-02-0108:40 AM
Hi,
This UPS has two outlet groups. Battery/Surge and Surge only. During a power outage the UPS provides output to the Battery/Surge outlets. The Surge only outlets are powered off.
Is the PC plugged into one of the Battery/Surge outlets and not a surge only outlet?
Does the UPS provide output to any of the Battery/Surge outlets when switched to battery?