Can someone tell me how much power a typical UPS would use while charging. Specifically, I need to know how the charging cycle works once a UPS has kicked in during a power loss and now has had its power supply restored so that it is now in "recharge" mode. I am trying to estimate power usage/needs for an emergency generator. For instance, if we have a power outage and roll out then start up a generator, will the UPCs running off of that generator use the kind of power I think they might? (It looks like a 120V, 12A UPC would charge at 1440 watt load.). Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:33 PM . Last Modified: 1 month ago
Can someone tell me how much power a typical UPS would use while charging. Specifically, I need to know how the charging cycle works once a UPS has kicked in during a power loss and now has had its power supply restored so that it is now in "recharge" mode. I am trying to estimate power usage/needs for an emergency generator. For instance, if we have a power outage and roll out then start up a generator, will the UPCs running off of that generator use the kind of power I think they might? (It looks like a 120V, 12A UPC would charge at 1440 watt load.). Thanks.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:33 PM . Last Modified: 1 month ago
Tom,
Can you provide a few base model numbers. The capacity differs based on the UPS, and I should be able to look up the information for you.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:33 PM . Last Modified: 1 month ago
The 1400 would use 136W for the battery charger.
Are there any other UPS's where the sepcs can be referenced for either yourself, or the thread starter
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:33 PM . Last Modified: 1 month ago
According to APC Doc #504, the Matrix UPS charging power is as follows:
1-2 smartcells: 500 watts
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 06:33 PM . Last Modified: 1 month ago
Can someone tell me how much power a typical UPS would use while charging. Specifically, I need to know how the charging cycle works once a UPS has kicked in during a power loss and now has had its power supply restored so that it is now in "recharge" mode. I am trying to estimate power usage/needs for an emergency generator. For instance, if we have a power outage and roll out then start up a generator, will the UPCs running off of that generator use the kind of power I think they might? (It looks like a 120V, 12A UPC would charge at 1440 watt load.). Thanks.