Follow along for an enriching discussion with our CEO, Peter Herweck, and industry leaders for a captivating Global Keynote at #InnovationSummit Paris 2024. Watch recording and join the #ImpactMaker movement!️
Emergency off button integrated to external system
APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Send a co-worker an invite to the portal.Just enter their email address and we'll connect them to register. After joining, they will belong to the same company.
You have entered an invalid email address. Please re-enter the email address.
This co-worker has already been invited to the Exchange portal. Please invite another co-worker.
Please enter email address
Send InviteCancel
Invitation Sent
Your invitation was sent.Thanks for sharing Exchange with your co-worker.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-2002:29 AM
Emergency off button integrated to external system
How does one integrate the emergency off button (EPO/EMO) circuit of an Smart-UPS SRT 5000 (SRT5KXLI) to an external system with its own 24V emergency off circuit?
There is some information in the manual about EPO but not how/if possible to connect to an external system.
Basically I want to use the existing emergency off button on the external system to also shut down the UPS at the same time.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-10-2112:27 AM
You'll want the external system to provide a dry contact output, either normally open or closed and wire it up the way it says on page 26 of the manual.
If the external system only provides some form of powered output, you'll want to put a relay between it and the UPS.