Posted: 2021-06-28 05:51 PM
This question was originally posted by Cricou on APC forums on 8/10/2020
Hello
I've an issue from several weeks
i've an EASY UPS BV 1 000 VA - 600W of maximum power
when i plugged on UPS the PS4 pro and the TV, and a power outage comes, the PS4 Pro is restarting and not the TV
the PS4 and TV are plugged into the Same plug !!
the total power used by PS4 pro and TV are 350W ....
Do you think the micro sut during the switch-over AC is too long for the PS4 ?
tks for your help
Posted: 2021-06-28 05:51 PM
This reply was originally posted by Cricou on APC forums on 8/11/2020
Thanks Gavan
do you know wich type or UPS and technolgy use to avoid time transfert too long ?
many thanks
Posted: 2021-06-28 05:51 PM
This reply was originally posted by Gavan on APC forums on 8/11/2020
Does the PS4 reboot straight away? If so then it sounds like it might be to sensitive to the transfer time.
Does it happen both when gaming and when the the PS4 is ideal?
-Gavan
Posted: 2021-06-28 05:51 PM
This reply was originally posted by Cricou on APC forums on 8/11/2020
hello , thanks for your reply
Yes PS4 is rebooting straight away...TV is still powered on without issue
i think also the transfer time is too long for PS4
but it appears only when PS4 is in HIGH Load (in gaming) not in Idle time....
Posted: 2021-06-28 05:51 PM
This reply was originally posted by Gavan on APC forums on 8/11/2020
It's probably a case that during high load (gaming) the PS4 is draining the capacitors in its power supply before the battery can kick in, unfortunately there is not a lot that can be done to resolve this.
-Gavan