Battery initial current and UPS max charging battery current?

Solved
dorffi_apc
Crewman
Crewman
0 Likes
3
218

Battery initial current and UPS max charging battery current?

This was originally posted on APC forums on 12/24/2016


I have APC ES 550 ups, 12V 7.2Ah, battery initial current is max. 2.16A.
Do you know how much ( Amps) this UPS charging battery max.?
I don`t think that it is 2.16A .
There must be current limitation circuit in device, with factor of safety.

thank you:)


Accepted Solutions
UnexpectedBill_apc
Captain
Captain
0 Likes
0
218

Re: Battery initial current and UPS max charging battery current?

This was originally posted on APC forums on 12/24/2016


I've never seen the charging current in one of these units go much past half an amp. It might get up to 750mA or so with a thoroughly depleted battery.

See Answer In Context

dorffi_apc
Crewman
Crewman
0 Likes
0
218

Re: Battery initial current and UPS max charging battery current?

This was originally posted on APC forums on 12/25/2016


thank you, for reply

That initial current is little mystery to me, is it charging start current or similar?

If battery has initial current 2.16A max. is there current limiter inside battery like feature.?

See Answer In Context

3 Replies 3
UnexpectedBill_apc
Captain
Captain
0 Likes
0
219

Re: Battery initial current and UPS max charging battery current?

This was originally posted on APC forums on 12/24/2016


I've never seen the charging current in one of these units go much past half an amp. It might get up to 750mA or so with a thoroughly depleted battery.

dorffi_apc
Crewman
Crewman
0 Likes
0
219

Re: Battery initial current and UPS max charging battery current?

This was originally posted on APC forums on 12/25/2016


thank you, for reply

That initial current is little mystery to me, is it charging start current or similar?

If battery has initial current 2.16A max. is there current limiter inside battery like feature.?

Brad_C_apc
Commander
Commander
0 Likes
0
218

Re: Battery initial current and UPS max charging battery current?

This was originally posted on APC forums on 12/26/2016


On 26/12/2016 3:01 AM, Keijo said:

If battery has initial current 2.16A max. is there current limiter inside battery like feature.?

No, that is the maximum charge current the manufacturer says you can squeeze into the battery without damaging it. You *can* charge them faster than that but it's really abuse that will shorten the ultimate battery life.