APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:21 AM . Last Modified: 1 week ago
Got one of these units a couple of weeks ago mainly because brownouts cause my home ADSL modem/ router to drop out. This means it comes back with a new IP address and that can cause problems with email blacklists.
So I was hoping that once I found a "good" IP address the router would keep hold of it by staying powered up.
Unfortunately, the BE700G just doesn't catch these interuptions - had one today and everything went off. Power came straight back but everything connected - LCD monitor, NAS, Printer and the modem/router all had powered down and back again.
I've got it set on max sensitivity, but am I just expecting too much for it to catch glitches?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:21 AM . Last Modified: 1 week ago
Got one of these units a couple of weeks ago mainly because brownouts cause my home ADSL modem/ router to drop out. This means it comes back with a new IP address and that can cause problems with email blacklists.
So I was hoping that once I found a "good" IP address the router would keep hold of it by staying powered up.
Unfortunately, the BE700G just doesn't catch these interuptions - had one today and everything went off. Power came straight back but everything connected - LCD monitor, NAS, Printer and the modem/router all had powered down and back again.
I've got it set on max sensitivity, but am I just expecting too much for it to catch glitches?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:21 AM . Last Modified: 1 week ago
Sorry not to reply - been travelling for a couple of days.
Yanked the mains plug out and it worked perfectly - modem/router stayed up which is precisely as I'd hoped.
So I guess the issue is exactly as you suggested - that the switchover point is at too low a voltage so when the voltage dips for a time it doesn't switch to battery but the voltage is too low to hold the connected equipment up.
It's all connected through wallwarts or power bricks and I had thought that might be a good thing as the voltage input range is usually pretty wide.
Message was edited by: Rory
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 04:21 AM . Last Modified: 1 week ago
Got one of these units a couple of weeks ago mainly because brownouts cause my home ADSL modem/ router to drop out. This means it comes back with a new IP address and that can cause problems with email blacklists.
So I was hoping that once I found a "good" IP address the router would keep hold of it by staying powered up.
Unfortunately, the BE700G just doesn't catch these interuptions - had one today and everything went off. Power came straight back but everything connected - LCD monitor, NAS, Printer and the modem/router all had powered down and back again.
I've got it set on max sensitivity, but am I just expecting too much for it to catch glitches?
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.