Back-UPS XS 1500 (beige)

Solved
uplandmad_apc
Cadet
0 Likes
1
56

Back-UPS XS 1500 (beige)

This was originally posted on APC forums on 9/26/2011


I have a Back-UPS XS 1500 that has been showing a battery warning. I recently replaced the battery, but it still shows the battery warning, and presumably will do so until the next time it runs (and passes) the battery self-test. I don't want to wait up to 2 weeks for this to occur during its normal schedule, as I suspect there may be another problem with the unit. How can I initiate the self-test manually, without powering down or dropping the existing load?

Message was edited by: uplandmad

Message was edited by: uplandmad


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
56

Re: Back-UPS XS 1500 (beige)

This reply was originally posted by Angela on APC forums on 9/26/2011


push the power button once - don't hold it down. this will manually execute a self test.

i referenced this user's guide if you'd like to double check -> http://www.apcmedia.com/salestools/ASTE-6Z7V72_R0_EN.pdf

See Answer In Context

1 Reply 1
BillP
Administrator Administrator
Administrator
0 Likes
0
57

Re: Back-UPS XS 1500 (beige)

This reply was originally posted by Angela on APC forums on 9/26/2011


push the power button once - don't hold it down. this will manually execute a self test.

i referenced this user's guide if you'd like to double check -> http://www.apcmedia.com/salestools/ASTE-6Z7V72_R0_EN.pdf