Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79337members
344031posts

Back-UPS Pro 650

Solved
Bob123456_apc
Crewman
Crewman
0 Likes
5
180

Back-UPS Pro 650

This was originally posted on APC forums on 9/27/2011


I have an old Back-UPS 650, the battery is dead. With the Battery removed should any of the lights on the front display light up when plugged into the wall?

Trying to figure out if this thing works and worth buying a battery.....

When I plug it into the wall the surge outlets work but of course not the battery side, but no LEDs on the front come on, not even the bad battery one.....

Message was edited by: Bob123456


Accepted Solutions
Bob123456_apc
Crewman
Crewman
0 Likes
0
180

Re: Back-UPS Pro 650

This was originally posted on APC forums on 9/30/2011


Perfect, thank you so much Jon!

See Answer In Context

5 Replies 5
johnsonzb_apc
Cadet
0 Likes
0
180

Re: Back-UPS Pro 650

This was originally posted on APC forums on 9/28/2011


Hi Bob,

If need, we can provide batteries and solution for you.

We mainly produce LiFePO4 batteries used for UPS, EV etc for nearly 10 years. good quality and price.

You are welcome to www.optimumchina.com for more information, any questions, please kindly let me know.

Looking forward to hearing from you asap.

Best regards,
Johnson

Optimum Battery Co.,Ltd
Mail: optimum9@optimum-china.com
MSN: johnsonzb@hotmail.com
Skype: johnsonzb
Mobile phone: +8615012704965
Tel: +86755-84630787
Fax: +86755-84630785

BillP
Administrator Administrator
Administrator
0 Likes
0
180

Re: Back-UPS Pro 650

This reply was originally posted by Dakota on APC forums on 9/28/2011


What is the EXACT model number of the ups and serial number


Do you have access to a decient mulitmeter or preferably a true RMS meter
If so what is the voltage of the battery

Bob123456_apc
Crewman
Crewman
0 Likes
0
180

Re: Back-UPS Pro 650

This was originally posted on APC forums on 9/28/2011


The model number is BP650S. I do have a nice Fluke 115 True RMS digi voltometer, and the batter is dead dead. Its not even installed, I've already recycled it.

My question is regarding the 4 LEDs on the front panel. Should they light up with no battery?

BillP
Administrator Administrator
Administrator
0 Likes
0
180

Re: Back-UPS Pro 650

This reply was originally posted by Jonathan on APC forums on 9/30/2011


Hi Bob,

I was able to locate the user manual for this UPS, you might want to check it for your reference. [BP650S User Manual|http://www.apcmedia.com/salestools/ASTE-6Z7UY5_R0_EN.pdf].

Basically, the BP650S would not turn on unless a good working battery is installed. Which means that the Front LEDs would not illuminate as well.

Bob123456_apc
Crewman
Crewman
0 Likes
0
181

Re: Back-UPS Pro 650

This was originally posted on APC forums on 9/30/2011


Perfect, thank you so much Jon!