This question was originally posted by chris on APC forums on 9/28/2007
I just bought the unit a month ago. My wife pluged a window unit into it on accident. No everytime we turn it on it last about 5-10 seconds and shuts off with the loud whistle tone. Can anyone help me fix the problem or is it fried?
Thank you for the help
Posted: 2021-06-28 08:00 PM
This was originally posted on APC forums on 10/3/2007
please email me if you have any questions on UPS systems..
prep71@hotmail.com
Posted: 2021-06-28 08:00 PM
This was originally posted on APC forums on 10/1/2007
Does it do the same thing if you turn it on with nothing plugged into it? Have you verified that both the red and black battery leads are connected? If yes to both, it sounds like the UPS may need to be replaced.
Posted: 2021-06-28 08:00 PM
This reply was originally posted by Oscar on APC forums on 10/1/2007
A window unit??
Try it with a small load, for example, a lamp. Then do a pull plug test.