Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79290members
343968posts

BR900GI make my PC power-on by itself when running on battery

Solved
cap_zone_apc
Crewman
Crewman
0 Likes
5
160

BR900GI make my PC power-on by itself when running on battery

This was originally posted on APC forums on 7/29/2013


PC setting : power-off and connect with usb data port. / Bios setting : Enable power-on by usb mouse/keyboard.

Problem occur when BR900GI starting run on battery, it make my PC power-on by itself.

This problem not happen if disconnect usb data port or disable power-on by mouse in bios.

Can I fix this problem? or It is a normal situation for apc ups. (My old local brand ups doesn't have this problem)

Thanks.


Accepted Solutions
cap_zone_apc
Crewman
Crewman
0 Likes
0
160

Re: BR900GI make my PC power-on by itself when running on battery

This was originally posted on APC forums on 7/31/2013


Thank Bill. I really appreciate for your help. smile

See Answer In Context

5 Replies 5
cap_zone_apc
Crewman
Crewman
0 Likes
0
160

BR900GI make my PC power-on by itself when running on battery

This was originally posted on APC forums on 7/29/2013


PC setting : power-off and connect with usb data port. / Bios setting : Enable power-on by usb mouse/keyboard.

Problem occur when BR900GI starting run on battery, it make my PC power-on by itself.

This problem not happen if disconnect usb data port or disable power-on by mouse in bios.

Can I fix this problem? or It is a normal situation for apc ups. (My old local brand ups doesn't have this problem)

Thanks.

cap_zone_apc
Crewman
Crewman
0 Likes
0
160

Re: BR900GI make my PC power-on by itself when running on battery

This was originally posted on APC forums on 7/29/2013


My OS is Win7 64bit and PowerChute Personal Edition v3.0.2.

cap_zone_apc
Crewman
Crewman
0 Likes
0
160

Re: BR900GI make my PC power-on by itself when running on battery

This was originally posted on APC forums on 7/31/2013


This problem still there it very annoy me. Sometime at night when blackout I have to get up to shutdown my pc again. frown

Shoud I RMA this ups?

BillP
Administrator Administrator
Administrator
0 Likes
0
160

Re: BR900GI make my PC power-on by itself when running on battery

This reply was originally posted by Bill on APC forums on 7/31/2013


You should not RMA the UPS. PowerChute cannot restart your computer if it is in a powered down state (S4 or S5). It will restart the computer if it is in sleep mode or standby and it is designed to do so in the event of a power failure. PowerChute wakes the system to allow it to power down properly before the UPS battery dies.

To resolve the issue power down the system completely.


cap_zone_apc
Crewman
Crewman
0 Likes
0
161

Re: BR900GI make my PC power-on by itself when running on battery

This was originally posted on APC forums on 7/31/2013


Thank Bill. I really appreciate for your help. smile