Posted: 2021-06-28 08:24 AM
This was originally posted on APC forums on 1/17/2020
I'm sure this has come up often, but I have a BR1500G, running at 7% load. The unit estimates 15 minutes or so of runtime, which seems very low at 7% load. I bought a new battery, but get the same results. Is this what I should expect? If not, how can I fix the problem? Thanks!
Posted: 2021-06-28 08:24 AM
This was originally posted on APC forums on 1/19/2020
Found a PC, installed the software, ran it, and updated the battery installation date. Runtime jumped from 14 minutes to 84 minutes. We'll have to check and see if that's accurate, but it's a lot closer to the advertised runtime, so I guess we'll let it go for now. Thanks!
Posted: 2021-06-28 08:24 AM
This reply was originally posted by Bill on APC forums on 1/17/2020
Hi,
Did you update the battery install date? In most cases when you update the install date the UPS recognizes the new battery and reports the correct run-time.
Posted: 2021-06-28 08:24 AM
This was originally posted on APC forums on 1/17/2020
Appreciate it, but I don't see how to do that. I have a mac, and no way to run the software. Can this be done from the unit itself? Thanks!
Posted: 2021-06-28 08:24 AM
This was originally posted on APC forums on 1/19/2020
Found a PC, installed the software, ran it, and updated the battery installation date. Runtime jumped from 14 minutes to 84 minutes. We'll have to check and see if that's accurate, but it's a lot closer to the advertised runtime, so I guess we'll let it go for now. Thanks!