APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:48 PM . Last Modified: 3 weeks ago
So I have a BE600M1 connected to my computer and one(1) monitor, my computer at max power pulls more than the 600, but even when not on battery power and running off the AC, I get the overload constant tone (when running something heavy on my computer), is this normal and am I just going to need to get a larger UPS, or is there something wrong with my UPS?
I'm new to using these at home, though we have dozens of them at work, usually our PML handles issues with them.
I appreciate any help y'all can offer, thank you!
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:48 PM . Last Modified: 3 weeks ago
Hi Bryn,
The BE600M1 provides 600VA not 600 watts. That particular unit is only rated to provide 330 watts peak.
In general the watt out put is the VA rating multiplied by the power factor, so a 1000VA unit with a power factor of .8 will provide 800 watts (roughly).
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 06:48 PM . Last Modified: 3 weeks ago
Hi Bryn,
The BE600M1 provides 600VA not 600 watts. That particular unit is only rated to provide 330 watts peak.
In general the watt out put is the VA rating multiplied by the power factor, so a 1000VA unit with a power factor of .8 will provide 800 watts (roughly).
-Gavan
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.