APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:06 AM . Last Modified: 2024-03-21 05:08 AM
I recently replaced the batteries in my BACK-UPS XS 900 and it wont charge them beyond 91%. I've tried two different sets of batteries and it has once or twice gone over 91% but it always seems to settle back down to displaying that level of charge in PowerChute.
Powerchute shows "Remainging battery charge: 91%" and shows "Battery is currently: Charging"
Any idea how I can recalibrate the charge level. I tried running down the UPS on battery to around 7% and then recharging.
Windws 7 Professional
Powerchute 3.0.0.1
Thanks, Tom
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:06 AM . Last Modified: 2024-03-21 05:08 AM
Hi Tom,
In performing manual runtime calibration, please follow these steps:
1. The UPS must have at least a 30% load on it during the calibration.
2. The load cannot fluctuate more than +/- 5% during the calibration.
3. Unplug the UPS from the input source and let it run on battery until it gets discharged.
4. Charge up the UPS/battery back to 100%
In addition to the abovce conditions, any UPS monitoring/shutdown software should be stopped from running in the background, and the serial cable should be detached from the UPS. This is necessary in order to prevent the software from shutting down the server/UPS due to an on-battery or low-battery condition
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 07:06 AM . Last Modified: 2024-03-21 05:08 AM
Hi Tom,
In performing manual runtime calibration, please follow these steps:
1. The UPS must have at least a 30% load on it during the calibration.
2. The load cannot fluctuate more than +/- 5% during the calibration.
3. Unplug the UPS from the input source and let it run on battery until it gets discharged.
4. Charge up the UPS/battery back to 100%
In addition to the abovce conditions, any UPS monitoring/shutdown software should be stopped from running in the background, and the serial cable should be detached from the UPS. This is necessary in order to prevent the software from shutting down the server/UPS due to an on-battery or low-battery condition
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.