APC UPS for Home and Office Forum
Support forum to share knowledge about installation and configuration of APC offers including Home Office UPS, Surge Protectors, UTS, software and services.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:43 AM . Last Modified: Friday
I'm having trouble figuring out what the best UPS is for my Mac Pro. It's the previous generation (Early 2008), not the most recent, and I have a pair of internal drives and a pair of Dell 21-inch LCD monitors attached to it. It replaced a Power Mac G5 that was running from an APC BackUPS Pro 1000 with no problems, and for the first month or two, I didn't see any troubles.
The problem started when I began (after some long offsite backups finally completed) to sleep the Mac Pro at night and wake it in the morning. About 20% of the time (a guess), the UPS would start screeching and shut off, powering down the Mac as well, which is just the opposite of why you use a UPS. 🙂 However, it never seemed to have trouble on a cold boot, and it could run the Mac fine when I removed wall power from the UPS.
I unplugged the Mac Pro from the UPS and attached it to a Watts Up power meter, where I learned that although the system draws only about 400W in normal usage, the inrush current at startup can range from nearly 800W to slightly over 1000W (and removing the monitors from the equation isn't sufficient to help, since they don't suck much power at startup). The Watts Up records the highest power draw in a session, and from what I can tell from watching, a high inrush current is actually fairly unusual - usually what happens is that I get a high maximum on a particular boot session fairly early, and then no matter how many times I sleep and wake the Mac Pro, the max inrush won't go any higher.
So, I'm OK with the fact that I need a new UPS - the BackUPS Pro 1000 is rated for only 650W and is a little old, so it probably isn't fully capable anyway. But the question is which one to get.
The $250 BackUPS RS 1500 would seem like a reasonable step up, but it supposedly maxes out at 850W, and I've seen several maximum inrush currents over that. Then there's the SmartUPS 1500, which supposedly maxes out at 980W but costs more than twice as much, at $560. I also gather the SmartUPS has pure sine wave output, as opposed to stepped output, but I don't understand how that is better or if it's relevant to this situation.
My goal is protection of the system, not runtime. I'd be happy with a 5-10 minute runtime - just enough time to shut down or sleep. So I'm somewhat bothered at the thought of having to pay a lot more for a UPS that's massively overspecced, just because it's the only way to get one that doesn't fail instantly if the inrush current is too high.
Suggestions about how to proceed?
cheers... -Adam
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:44 AM . Last Modified: Friday
You would need to check the tech specs for your system on the Apple website. Many times they don't list the nitty gritty details like power factor and PFC yes/no/type, and only give you the voltage and amp rating. You will probably end up needing to call Apple and request the information, or check their forums.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:43 AM . Last Modified: Friday
So the current line of BackUPS devices, if the inrush current is at all above that 850W spec, will still just shut off (I've seen a couple of instances above 850W)? But a SmartUPS, if the inrush current is slightly above its spec (I've seen only one inrush draw above 1000W) won't?
I guess I'm a little confused as to why the high draw would cause the UPS to shut off when the wall circuit behind it can handle the draw - it's not as though the circuit is failing such that the UPS has to, on its own, provide that much power. And since the UPS is kicking over from the circuit to the battery very quickly in the event of a power failure, it would seem that it's normally acting as a passthrough.
Or am I just not understanding some basic chunk of how these devices are designed?
And how does the sine wave capability play into this?
cheers... -Adam
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:43 AM . Last Modified: Friday
If you have seen inrushes higher than what the Back-UPS RS 1500 can handle then it's hard to recommend it without some sense of hesitation. If you know the # of inrush occurrences will be limited you could certainly get away with using the UPS without worrying about an overload. Our Back-UPS units started getting retooled in mid 2008 to be more (not perfectly) compatible with higher-inrush PFC devices, by widening transfer times for state changes and calibrating/improving capacitor (smoother transitions, more power "ridethrough") functionality. This basically means the units do not hiccup or drop PFC loads nearly as often as older models do. Does this mean they are perfect with PFC devices? No, and that is especially true with larger active PFC power supplies...we still recommend Smart-UPS for those.
An SUA1500 will most certainly be able to handle your Mac Pro. Smart-UPS units have been working well with PFC power supplies on datacenter-grade servers and devices for some time now. It's really a decision that's left up to your "risk tolerance".
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:43 AM . Last Modified: Friday
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:44 AM . Last Modified: Friday
Thanks so much for the details! One last thing. I'm having trouble finding any information about the power supply in the Mac Pro. How can one tell if it's an Active-PFC power supply (and what does that mean)? Can you point me to any discussions of that?
cheers... -Adam
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-29 12:44 AM . Last Modified: Friday
You would need to check the tech specs for your system on the Apple website. Many times they don't list the nitty gritty details like power factor and PFC yes/no/type, and only give you the voltage and amp rating. You will probably end up needing to call Apple and request the information, or check their forums.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.