Dears
I have two "Smart-UPS VT 30 kVA" UPS. Please help me. Advice any idea. Sometimes it is OK. Sometimes is below issue.
Thanks
Chuluunbaatar
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:39 AM . Last Modified: yesterday
Hi,
The UPS is alarming because the incoming voltage or frequency is out of range. The understanding I have is the VT 30 should have shipped with a network management card (NMC). If you look at the NMC data log you will see information on the incoming voltage and frequency. You can use that information to get the issue resolved.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:39 AM . Last Modified: yesterday
In addition to what Bill said, the events you're seeing basically say:
Although there's a problem with the input voltage, the SmartUPS VT is double-conversion so the computers and other loads attached to the UPS get completely clean voltage from the UPS. Ordinarily if something is wrong with the UPS such as a failed electrical component, it can bypass itself and feed the input voltage directly to the attached loads. But it won't do so if there's a problem with the input voltage. So even though it's not a problem now, if the input is frequently bad, you might want to investigate the cause.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:39 AM . Last Modified: yesterday
Hi,
The UPS is alarming because the incoming voltage or frequency is out of range. The understanding I have is the VT 30 should have shipped with a network management card (NMC). If you look at the NMC data log you will see information on the incoming voltage and frequency. You can use that information to get the issue resolved.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:39 AM . Last Modified: yesterday
In addition to what Bill said, the events you're seeing basically say:
Although there's a problem with the input voltage, the SmartUPS VT is double-conversion so the computers and other loads attached to the UPS get completely clean voltage from the UPS. Ordinarily if something is wrong with the UPS such as a failed electrical component, it can bypass itself and feed the input voltage directly to the attached loads. But it won't do so if there's a problem with the input voltage. So even though it's not a problem now, if the input is frequently bad, you might want to investigate the cause.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:40 AM . Last Modified: yesterday
Thanks
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 03:40 AM . Last Modified: yesterday
thank you very much