Posted: 1 week ago
Hello,
I have an issue where a SMX750i is failing upgrade at 7%, obviously it starts the process and switches the UPS off, then that's where it stays.
I have installed a new battery pack - still fails the same
I have tried with UPS switched off - still fails the same
I would like to think I am doing everything right as I have no problem with other APC UPS's when using the same FirmwareUpgradeWizard_v4.2.1
UPS Firmware details:
UPS 09.1
MCU 09.1
UBL50E.7
MBL 06.0
The tool automatically selects SMT20UPS_10-2.enc
Any assistance would be great as I would really like to be able to enable the Modbus communications that the later firmware supports.
Posted: Wednesday
Hi Matt,
Thanks for the advice, I must admit I did try and download v4.3 but that was only available outside of UK, seems like they have released it here now, the firmware file is the same.
What I did read on here is that someone had issue and were advised to do a factory reset if they had the 5 button version, I done that and found that upgrade via USB still failed but via serial then worked, so yesterday I was successful lifting it to v10.2 and giving me the Modbus communication.
Thanks again, and hopefully this will help anyone else with similar issues.
Posted: Wednesday
Hi Ghoster
Could you try the latest firmware upgrade wizard 4.3.0 and see if that helps.
https://www.apc.com/uk/en/faqs/FA279197/
If it doesn't I can decode the FUW.log file it produces and see if that highlights the issue.
Thanks
Matt
Posted: Wednesday
Hi Matt,
Thanks for the advice, I must admit I did try and download v4.3 but that was only available outside of UK, seems like they have released it here now, the firmware file is the same.
What I did read on here is that someone had issue and were advised to do a factory reset if they had the 5 button version, I done that and found that upgrade via USB still failed but via serial then worked, so yesterday I was successful lifting it to v10.2 and giving me the Modbus communication.
Thanks again, and hopefully this will help anyone else with similar issues.