Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79289members
343963posts

smart ups battery issues

Solved
DaveCCAC_apc
Crewman
Crewman
0 Likes
3
150

smart ups battery issues

This was originally posted on APC forums on 11/10/2016


Hello, I have a Smart-UPS X 3000  that is reporting errors, and I am looking for some help before I replace the whole unit.

The UPS has a network management card in it, and about a week ago it started reporting "Battery High Voltage Violation" after what the logs show as  "Compensating for a high input voltage" event.

The battery tray was swapped out with a new APC tray, and UPS was also restarted, since then the logs are reporting the following every 30 seconds.

UPS: A battery charger fault exists.
UPS: A battery charger fault no longer exists.

The measurements status page looks find, but the batteries are never charging:

Status Smart-UPS X 3000

Last Battery Transfer: Unknown
Internal Temperature: 20.8°C
Runtime Remaining: 32min 38sec
UPS Input
Input Voltage: 115.1 VAC @ 60.0 Hz

UPS Output
Output Voltage: 115.1 VAC @ 60.0 Hz
Load Current: 4.4 Amps

Output VA: 17.5 %
Output Watts: 17.8 %
Output Efficiency: 93.9 %
Output Energy Usage: 0.34 kWh
Battery Status
Battery Capacity: 65.7 %
Battery Voltage: 128.7 VDC
Num of External Batteries: 0 

The about page shows the following:


About UPS

Model: Smart-UPS X 3000
Serial Number: IS1232000296
Firmware Revision: UPS 01.9 / COM 01.6 / UBL 03.2 / CBL 06.0 (ID10)
Manufacture Date: 07/30/2012

Apparent Power Rating: 2880 VA
Real Power Rating: 2700 W

Is there a reset that will fix this? or am I looking at replacing the UPS?

Thanks,


Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
150

Re: smart ups battery issues

This reply was originally posted by Gareth on APC forums on 11/15/2016


I had this. It turns out the UPS was reading the battery about 6 volts higher than it was. I replaced it.

See Answer In Context

3 Replies 3
UnexpectedBill_apc
Captain
Captain
0 Likes
0
150

Re: smart ups battery issues

This was originally posted on APC forums on 11/11/2016


The UPS may have suffered a failure, but there is a reset procedure you can try. This will require powering down the attached load.

Safely power down the attached load. Turn off the UPS and disconnect it from AC power. Disconnect all internal batteries and any external battery packs if you have them. Depress the power button on the UPS for a few seconds. You may see the LEDs and display flash, hear some beeping and a few clicks. Leave it alone for a minute or two afterwards.

Reconnect all the batteries and connect the unit back to AC line power. I'd test it and see if it seems to be working properly before reattaching your load.

This unit would appear to be a newer MicroLink model, and as such, it should have upgradeable firmware. You might want to check and be sure that the unit is running the latest firmware available. (This should not be confused with firmware for the network management card.)

DaveCCAC_apc
Crewman
Crewman
0 Likes
0
150

Re: smart ups battery issues

This was originally posted on APC forums on 11/15/2016


Thanks for the reply.

We will schedule an outage this week and let you how we make out.

BillP
Administrator Administrator
Administrator
0 Likes
0
151

Re: smart ups battery issues

This reply was originally posted by Gareth on APC forums on 11/15/2016


I had this. It turns out the UPS was reading the battery about 6 volts higher than it was. I replaced it.