Invite a Co-worker
Send a co-worker an invite to the Exchange portal.Just enter their email address and we’ll connect them to register. After joining, they will belong to the same company.
Send Invite Cancel
79472members
344257posts

powerchute fails authentication with NMC

Solved
zukic_apc
Ensign
Ensign
0 Likes
2
295

powerchute fails authentication with NMC

This was originally posted on APC forums on 8/19/2016


hi all

im trying to setup powerchute but the authentication with the NMC keeps failing
i get the following error

The security details provided do not match the settings on NMC(s): xx.xx.xx.xx
im using the default username and password, apc/apc
and the authentication phrase has been set correctly on the NMC and then added to powerchute.
the authentication phrase was set under configuration -> sync control
i assume this is the only place it needs to be set?

i can browse to both NMC and powerchute management pages.
here is the NMC details
Model: Smart-UPS SRT 5000
SKU: SRT5KRMXLI
Firmware Revision: UPS 04.0 (ID1013)
Manufacture Date: 14.10.2015
Hardware Factory
   
Model Number: AP9537SUM
Hardware Revision: 05
Manufacture Date: 10/05/2015
MAC Address:
Management Uptime: 0 Days 0 Hours 14 Minutes

Powerchute details

PowerChute Network Shutdown 4.1.0 Build 6428

any ideas why this isnt working?
let me know if you need any more details
appreciate any help
thanks!

Accepted Solutions
BillP
Administrator Administrator
Administrator
0 Likes
0
295

Re: powerchute fails authentication with NMC

This reply was originally posted by Angela on APC forums on 8/19/2016


You're welcome!

See Answer In Context

2 Replies 2
zukic_apc
Ensign
Ensign
0 Likes
0
295

Re: powerchute fails authentication with NMC

This was originally posted on APC forums on 8/19/2016


awesome!

yep that did the trick... thanks!

BillP
Administrator Administrator
Administrator
0 Likes
0
296

Re: powerchute fails authentication with NMC

This reply was originally posted by Angela on APC forums on 8/19/2016


You're welcome!