Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
You can subscribe to this forum after you log in or create your free account..
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.
Already have an account? Login
Posted: 2022-02-07 01:16 AM . Last Modified: 2022-02-07 01:17 AM
Hello,
We have AP8653 which had connectivity issues.
In log we get:
Rack PDU 1: NMC CAN bus off.
Rack PDU 1: NMC CAN bus off cleared.
Rack PDU 1: Component communications lost with Outlet Board 3 Meter. Please verify that a terminator is inserted in either the In or Out port.
Rack PDU 1: Component communications lost with Outlet Board 2 Meter. Please verify that a terminator is inserted in either the In or Out port.
Rack PDU 1: Component communications lost with Outlet Board 1 Meter. Please verify that a terminator is inserted in either the In or Out port.
Terminator is inserted in OUT port, we tried to switch LCD module with another one which is for sure working.
After total power cut, PDU work ok for 2-3 days and same story begin.
We have this firmware:
Firmware
Rack PDU
Version
6.8.0
Date
Jul 22 2019
APC OS (AOS)
Version
6.8.2
Date
Jul 22 2019
Boot Monitor
Version
1.0.9
Date
Mar 27 2019
Posted: 2022-02-07 02:02 AM . Last Modified: 2022-02-07 02:07 AM
Hi Michal
Apart from the swap of the display module, it might be worth it to swap to a CAN bus terminator that you know to be working, just to rule it out.
Apart from that, formatting the module (by logging on with SSH/telnet, and running the format command) and upgrading to latest firmware might also be an idea -> https://www.se.com/ww/en/download/document/APC_RPDU2G_706_EN/
If neither of the above makes any difference, I think the next step should be to open a case with your local customer care center as you might be looking at hardware issues.
You can find your local customer care, but visiting https://www.apc.com/us/en/support/contact-us/ and change country in the top left corner of the page.
Best regards
Tonny
Posted: 2022-02-07 02:21 AM
Hi TonKei,
Yes i tried 3 different terminators from other PDU.
Software update also don't change anything.
I'll open case with support if there is no other ideas here.
Thank you
User | Count |
---|---|
4835 | |
190 | |
111 | |
108 | |
67 | |
63 |
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.