Hello!
I use MAIN. SERV. BYPASS PANEL (SBP60KHC1M1) with Symmetra PX 40kVA. Pls tell me how works SBP60KHC1M1 . What switch I need turn to put my UPS to bypas mode? If I will turn Q003 switch is it enough? (http://www.apcmedia.com/salestools/ASTE-63XTVX_R0_EN.pdf)
Thanks!
Posted: 2021-06-26 03:40 AM
This was originally posted on APC forums on 7/1/2008
Hello!
I use MAIN. SERV. BYPASS PANEL (SBP60KHC1M1) with Symmetra PX 40kVA. Pls tell me how works SBP60KHC1M1 . What switch I need turn to put my UPS to bypas mode? If I will turn Q003 switch is it enough? (http://www.apcmedia.com/salestools/ASTE-63XTVX_R0_EN.pdf)
Thanks!
Posted: 2021-06-26 03:40 AM
This reply was originally posted by Doan on APC forums on 7/15/2008
hi,
First,you turn the UPS to bypass by powerview,still the yellow indicator (bypass)on .Now you can turn ON Q3 on Maintenance Bypass Panel.
Good luck.
Posted: 2021-06-26 03:40 AM
This was originally posted on APC forums on 7/1/2008
Hello!
I use MAIN. SERV. BYPASS PANEL (SBP60KHC1M1) with Symmetra PX 40kVA. Pls tell me how works SBP60KHC1M1 . What switch I need turn to put my UPS to bypas mode? If I will turn Q003 switch is it enough? (http://www.apcmedia.com/salestools/ASTE-63XTVX_R0_EN.pdf)