Posted: 2021-07-01 12:33 AM . Last Modified: 3 weeks ago
I have searched for an answer here but found nothing. I am running PCPE 3.0 and want to disable the popup notifications that happen every time the UPS switches in and out. We have a lot of noise on this AC feed and even at the lowest settings the UPS kicks in many times per hour. Can I turn off those messages that pop up off the lower right toolbar?
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 12:33 AM . Last Modified: 3 weeks ago
Hi actek, there is way to mute the alarms on the ups itself (so it will not make a beeping noise) however I believe in the cause of a transfer to battery a pop up notification will still come up letting you know the unit has changed state. Hope this helps.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-07-01 12:33 AM . Last Modified: 3 weeks ago
Hi actek, there is way to mute the alarms on the ups itself (so it will not make a beeping noise) however I believe in the cause of a transfer to battery a pop up notification will still come up letting you know the unit has changed state. Hope this helps.