Hello! I reviewed all of the manuals and searched through the knowledge base and forum posts, and have not found what I am looking for - the best practices steps when adding an XR unit to a live SY16K. I am terrified of ruining the batteries in the master frame and/or XR, or otherwise ruining the equipment! I am hopeful that one of the Symmetra gurus in this forum will be able to help me : ) I suppose I am looking for confirmation of what I am guessing would be the proper method with regard to the state of the master frame when connecting the XR unit's DC cable - bypass mode, or total shutdown, other? I know the steps from that point re: not adding the batteries until connected and communicating, etc.... I just want to know what is required for the master frame during the process, so I do not cause battery or other equipment issues. Thank you in advance for your help with this matter! rg
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:48 AM . Last Modified: 1 month ago
UPDATE: I successfully connected the XR to the master frame - first putting the master frame into bypass mode, and then taking the master frame out of bypass mode after I connected the power cable. I followed the prescribed procedures for the remainder of the setup, and all is well.
Link copied. Please paste this link to share this article on your social media post.
Link copied. Please paste this link to share this article on your social media post.
Posted: 2021-06-28 05:48 AM . Last Modified: 1 month ago
UPDATE: I successfully connected the XR to the master frame - first putting the master frame into bypass mode, and then taking the master frame out of bypass mode after I connected the power cable. I followed the prescribed procedures for the remainder of the setup, and all is well.
Link copied. Please paste this link to share this article on your social media post.
Create your free account or log in to subscribe to the forum - and gain access to more than 10,000+ support articles along with insights from experts and peers.